For several years I ran a 7.5hp IR 2 stage compressor off of a 30hp Phase-a-matic rotary phase converter. A few years back I upgraded to a 10hp 2 stage compressor, and could not get it to start under load off of the RPC. IT would start just fine if the compressor tank was empty, but if I tried to start it at the pressure kick-in (145psi), the motor would spin a few revolutions and then stall out when the compressor head starting developing back pressure. In order to make it work I had to install a pressure relief valve on the compressor head that is timed to close 8 seconds after the compressor kicks on (in order to allow the motor to come up to speed).
Basically the motor will spin up with no back pressure on the compressor, but if the tank is full it won't.
The compressor will start just fine w/o the relief valve if I'm running my 400hp generator and bypassing the RPC. So it appears that the RPC won't provide enough amperage to cover the high current inrush during the 5 seconds or so that it takes to spin up to speed off of the RPC when the tank is at pressure. When the generator is running, spin up time is less.
The external relief valved solve my problem, but I'm puzzled about why some folks recommend a VFD for a compressor. Will a VFD do a better job of providing full power through the start up current demand under load on a compressor than an RPC will? It seems to me that it wouldn't work
Basically the motor will spin up with no back pressure on the compressor, but if the tank is full it won't.
The compressor will start just fine w/o the relief valve if I'm running my 400hp generator and bypassing the RPC. So it appears that the RPC won't provide enough amperage to cover the high current inrush during the 5 seconds or so that it takes to spin up to speed off of the RPC when the tank is at pressure. When the generator is running, spin up time is less.
The external relief valved solve my problem, but I'm puzzled about why some folks recommend a VFD for a compressor. Will a VFD do a better job of providing full power through the start up current demand under load on a compressor than an RPC will? It seems to me that it wouldn't work