Shop43
Plastic
- Joined
- May 25, 2023
Hi,
Currently we power a 15+1.5+1 hp grinder. Our current place has 3phase And we use a 45 kva to 480 step up transformer. Startup draws 16 and idle goes down To single digit.
Our new shop, electric co wants to charge 50k for 3 phase power so weighing out expense instead 200 amp service single phase 120-240 service with a rotary phase converter option.
Electric co says these power draws will destroy residential neighborhood transformers. This does not seem accurate given that a a North American Phase converter PL-40 needs 100a breaker (Already talked to NorthAmerican and they said no problem)
What would you do?
thanks in advance!!